Shore power tripping
I know I’m no longer a Rinker owner, but this site is 100x better than the Four Winns forum…so I’m hoping someone can steer me in the right direction bc I’m not the smartest when it comes to electrical!?!
My power pedestal has newer gfi breakers for shore power. My boat is now tripping the breaker when there is a large draw. I’ve tried my neighbors outlet that has a gfi breaker with the same result. I tried two other power pedestals that don’t have gfi breakers and they never trip. So tonight I went down, shut off every breaker on the boat to try and isolate the issue, with no luck.
Just turning the battery charger on trips it.
Turning on all of the ac systems except the battery charger is fine, until I turn on the battery charger
Turning on all of the ac systems except the battery charger, then turn the air conditioner on is fine as long as it’s just the fan. When the compressor kicks in, it trips.
It seems like when there is a large draw is when it trips.
Any suggestions?
If it looks like your neutral and grounds in your 120v panel are not shared then make sure there is not a bonding bar connecting the two bars together.
You should be able to check continuity at the shore power plug on your boat and see if there is continuity between your neutral and ground as well.
Ground and neutral should only be bonded at the very beginning of the source such as the main breaker at the marina not in anything downline from that. Me and another member went thru every panel at our club and fixed everything we could find wrong and here we are a year later working on the last offending wires and panels.
If anything being turned on trips it that leads me to working around the shore power connections on the boat and also the bus bars.
You said the panel has newer GFI breakers so I thought this was a new install at the marina.
it turns out it was a bad heating element on the water heater. Here’s where I get lost…it would trip the breaker even when the circuit breaker was off for the heater. I actually found the answer to this problem on the Se* Ra* forum. I have been stumped for weeks now. I am certainly not an electrician, so I am wondering how it would trip the breaker with no power going to it. The other forum said they had the same issue.