cleaning out cleaning system from broken impeller...
rasbury
Member Posts: 8,433 ✭✭✭✭✭
I am really confused..on the other thread I have going, I ran my raw water pump dry and destroyed the impeller. I have the 1/2 closed loop system with a heat exchanger. I've been told to remove the end cap off the heat exchanger to clean out the bits-what I fail to understand is how the water gets into the tubes- if coolant surrounds the tubes and I pull the end cap off, aren't I just releasing the coolant? I would think I'd be pulling off a hose and back flushing the system to blow the bits back out, what am I missing?
Best Answers
-
Handymans342 Member Posts: 10,375 ✭✭✭✭✭Usually that end cap is Raw water side so you can remove it to clean the tubes.
-
LaRea Member, Moderator Posts: 7,766 modThe coolant is totally separated from the end cap. There might be a bit of raw water, but probably not more than a few teaspoons.
Answers
The raw water enters through the end cap, flows through a bundle of closed straight tubes, and exits through the other end cap. When you take off the end plate, you're looking lengthwise through the bundle of tubes. The coolant comes in through a separate entry, flows AROUND the tubes, and exits at the other end. The coolant has no direct contact with the raw water or the end caps.
The hot coolant heats up the bundle of tubes, and the raw water in the tubes carries the heat away.