Fridgerator troubles- Solved
Wildboating
Member Posts: 957 ✭✭✭
anyone a guru here? Here is what I am coming up with:
On 110vac:
25.66v going into control module
12.4v into transformer
No code flashing on 110 yet unit does not operate. Fan does come on
12v
1 flash on led, indicates low voltage according to manual I seen
12.2 into transformer
12.45 into control module
2003 Rinker 342 Fiesta Vee, 350 Mag MPI, Bravo 3 2.20:1 w/ 22p 4 x4 props
Post edited by Wildboating on
Comments
Just saying....
2002 FV 342 on Lake St. Clair - Past Commodore SHC - Vessel Examiner USCGAUX
2002 FV 342 on Lake St. Clair - Past Commodore SHC - Vessel Examiner USCGAUX
Update:
Swapped power supplies- still will not start
Swapped Controllers- no start
Checked voltage drop- .10v / 25.5-25.4. In range
Checked continuity from pins to case/ nothing
Checked Ohms across pins- 2.2 ohms. In range
Motor tries to start then immediately gets cut
I have exhausted all troubleshooting guides. Anyone else have another trick? I am getting single led flash- indicating low voltage.
I received a code on 12v and none on 110. However the compressor still would not start. After troubleshooting everything I came full circle back to this very statement. Why do I have code on 12v and not 110, what if even though I'm trying to start on 110 the controller knows there is something not right on the 12v line. I drop the 12v line from the invertor and like magic,, the compressor starts spinning! Now I need to recharge the refrigerant as there may be a pinhole leak. Our coldest setting dwindle over the last 2 years but a can of refrigerant every 2 years vs $1000 refrigerator I'm good with until I get other things fixed.
Now i I need to chase out why the controller does not like my 12v connection. Power is steady around 12.5, thinking bad breaker or loose/corroded connection.