Galvanic Isolator and AC Grounds

YYZRCYYZRC Member Posts: 5,470 ✭✭✭✭✭
edited July 2022 in Electrical Discussions
I am removing the starboard shore power inlets and replacing with an inverter circuit. 

The galvanic isolator as originally installed is wired as follows:

BOAT GROUND
Starboard shore power inlet grounds (??)
Generator ground (ok)
Panel ground bus bar (ok)

SHORE POWER GROUND
Port shore power inlet grounds (ok)

I don’t understand why the starboard shore power grounds were wired into the boat side of the galvanic isolator. 


2006 390 EC
2008 350 EC
Georgian Bay

Comments

  • GrahamuGrahamu Member Posts: 921 ✭✭✭
    A galvanic isolator is used to isolate the boat from shorepower ground and other boats. Don't understand why your genset is isolated.
  • YYZRCYYZRC Member Posts: 5,470 ✭✭✭✭✭
    The genny wasn’t isolated. The starboard shorepower were. 
    2006 390 EC
    2008 350 EC
    Georgian Bay
  • dalekdalek Member Posts: 260 ✭✭✭
    That's got to be a mistake. The port and starboard inlets should be together. If it were wired the way it was, the isolator would only work if you used the port inlet.
  • GrahamuGrahamu Member Posts: 921 ✭✭✭
    All shorepower grounds should be connected to one side of the isolator and the other side connected to ship grounds,
  • Pat310Pat310 Member Posts: 605 ✭✭✭
    @YYZRC are sure there is not a second isolator near the other shore power inlet?
  • YYZRCYYZRC Member Posts: 5,470 ✭✭✭✭✭
    Only one isolator. 

    This was meant as more of a PSA. For sure it was wired wrong from the factory. 